 Post subject: Triple Evacuation of refrigeration system
PostPosted: Mon Jun 21, 2004 12:14 pm 
Offline
User avatar

Joined: Tue Apr 13, 2004 3:25 am
Posts: 1947
Location: Texas
Chilly1 -

Evacuate to 500 microns, break vacuum to 0 psi with refrigerant (the one you wish to use in the system.) evac to 500 micron again and break vacume a second time to 0 psi as before. Now pull a vacuum to 250 microns this will take a few hours and will insure that the system is completly free of contaminants. Break vacuum to 0 psi and add the oil with an oil pump replacing the same amount you last removed. You then pull a vacuum to 500 microns. This compleats the clean and flush of your system. It may seem excessive to evacuate it so many times but it is the best way to insure a clean system .


Gary Lloyd -

I agree. A triple evacuation with a mediocre vacuum pump will do a better job than a single evacuation with the best pump on the market.

Another trick is to break the vacuum on the high side. This pushes the leftover residuals through the system to the low side. Then on the next evacuation, open the low side valve to the pump first.

If you have nitrogen available, the vacuum should be broken with nitrogen after the first evacuation. The compressor oil will not absorb the nitrogen, so the second evacuation will go much faster. This can save a lot of time.

_________________
Ron Image

Kicks just keep gettin harder to find
Want to learn the "T.E.C.H. Method"Click Here


Top
 Profile  
 
 Post subject:
PostPosted: Mon Jun 21, 2004 1:28 pm 
Offline
User avatar

Joined: Wed Jun 16, 2004 9:04 pm
Posts: 73
Location: Slovenia
How do you know by gauges when is 500 or 250 micron of vacum?


Top
 Profile  
 
 Post subject:
PostPosted: Tue Jun 29, 2004 3:10 pm 
Offline
User avatar

Joined: Wed May 12, 2004 3:45 pm
Posts: 333
sharp wrote:
How do you know by gauges when is 500 or 250 micron of vacum?


Well at sea level pressures :

0 mircons = 29.921 inhg
250 mircons = 29.91 inhg
500 mircons = 29.90 inhg

You'll need an electronic mircon guage to read the vacuum accurately though, as everyone says standard dial guages are not all that accurate. If this is wrong, please correct me. :)


Top
 Profile  
 
 Post subject:
PostPosted: Tue Jun 29, 2004 3:21 pm 
Offline
User avatar

Joined: Wed May 12, 2004 3:45 pm
Posts: 333
Ok ... Do I understand that the Best way to triple evac a system is :

1st evac from both the high and low sides open, close the low side, then break to 0 psi with N2 on the high side, close high side ... 2nd evac from low side then break vac to 0 psi with refrigerant of choice ( low side or high side break ? ) ... then finally low side evac, breaking to 0 psi again on low side. :?


Top
 Profile  
 
 Post subject:
PostPosted: Tue Jun 29, 2004 5:50 pm 
Offline
User avatar

Joined: Wed Jun 16, 2004 9:04 pm
Posts: 73
Location: Slovenia
Tnx

_________________
Drive fast as your guardian angel can fly.


Top
 Profile  
 
 Post subject:
PostPosted: Tue Jun 29, 2004 11:27 pm 
Offline
User avatar

Joined: Tue Apr 13, 2004 3:25 am
Posts: 1947
Location: Texas
Maybe Gary can give us a better answer on this.

I was never sure of how well I was vacuuming until I got a vacuum gauge. They are awesome! I found mine on e-bay for $60. It was well worth the money.

As far as I know, when your using your manifold gauges, you can only guess at how well of a vacuum your pulling.

_________________
Ron Image

Kicks just keep gettin harder to find
Want to learn the "T.E.C.H. Method"Click Here


Top
 Profile  
 
 Post subject:
PostPosted: Wed Jun 30, 2004 3:56 am 
Offline
User avatar

Joined: Wed May 12, 2004 3:45 pm
Posts: 333
HoboCrow wrote:
Ok ... Do I understand that the Best way to triple evac a system is :

1st evac from both the high and low sides open, close the low side, then break to 0 psi with N2 on the high side, close high side ... 2nd evac from low side then break vac to 0 psi with refrigerant of choice ( low side or high side break ? ) ... then finally low side evac, breaking to 0 psi again on low side. :?


Would you guys give this a reply ... treat it like an overclocked evac ... you know, the best first start to building a World Class system ... that's what we're after! :P


Top
 Profile  
 
 Post subject:
PostPosted: Wed Jun 30, 2004 10:13 am 
Offline
User avatar

Joined: Thu Apr 15, 2004 2:52 am
Posts: 180
Location: Trenton MI, USA
Back when I started in the trade, vacuum pumps were huge and heavy, and micron gauges were non-existant. There were very rare systems, primarily absorbers, that had vacuum pumps permanently installed. We used to pipe the vacuum pump discharge into a container of oil and count the bubbles per minute. For smaller systems we used a refrigerator compressor and triple evacuated, but not into microns. I tend to think of microns as overkill, but then I'm from the really old school.

_________________
Image

Author - Refrigeration Books

Want to learn more? Click Here


Top
 Profile  
 
 Post subject:
PostPosted: Wed Jun 30, 2004 2:28 pm 
Offline
User avatar

Joined: Wed May 12, 2004 3:45 pm
Posts: 333
LOL!! Ok Gary, I'll make sure I have a sight glass and a watch ... :D


Top
 Profile  
 
 Post subject:
PostPosted: Wed Jun 30, 2004 2:42 pm 
Offline
User avatar

Joined: Thu Apr 15, 2004 2:52 am
Posts: 180
Location: Trenton MI, USA
There are lots of newfangled gadgets out there, and it would be inexcusable for a professional not to have these, but I'm not certain that the extra expense is justified for the hobbyist, and it doesn't mean you can't do a good job. Back in the good old days, we built some top quality equipment and a lot of it is still working today.

_________________
Image

Author - Refrigeration Books

Want to learn more? Click Here


Top
 Profile  
 
 Post subject:
PostPosted: Wed Jun 30, 2004 11:34 pm 
Offline
User avatar

Joined: Tue Apr 13, 2004 3:25 am
Posts: 1947
Location: Texas
AAHH - "The Good Old Days" 8) - How sweet it was. :wink:

_________________
Ron Image

Kicks just keep gettin harder to find
Want to learn the "T.E.C.H. Method"Click Here


Top
 Profile  
 
 Post subject:
PostPosted: Thu Jul 01, 2004 4:09 am 
Offline
User avatar

Joined: Wed May 12, 2004 3:45 pm
Posts: 333
Gary Lloyd wrote:
There are lots of newfangled gadgets out there, and it would be inexcusable for a professional not to have these, but I'm not certain that the extra expense is justified for the hobbyist, and it doesn't mean you can't do a good job. Back in the good old days, we built some top quality equipment and a lot of it is still working today.


Hey Gary ... what! Did we miss your birthday or somthn ... :P


Top
 Profile  
 
 Post subject:
PostPosted: Tue Aug 03, 2004 6:00 pm 
Offline
User avatar

Joined: Mon Aug 02, 2004 7:59 am
Posts: 338
Is chilly1 saying that you need to take your oil b4 you vacuum and then put it back in?


Top
 Profile  
 
 Post subject:
PostPosted: Tue Aug 03, 2004 9:52 pm 
Offline
User avatar

Joined: Tue Apr 13, 2004 3:25 am
Posts: 1947
Location: Texas
JSU wrote:
Is chilly1 saying that you need to take your oil b4 you vacuum and then put it back in?


Chilly1 was answering a question for me when he made that post. At that time I had drained the oil out of a compressor because it was old and I was changing it. You don't need to change the compressor oil every time you evacuate the system.
Does that answer your question?

_________________
Ron Image

Kicks just keep gettin harder to find
Want to learn the "T.E.C.H. Method"Click Here


Last edited by runmc on Wed Aug 04, 2004 11:36 am, edited 1 time in total.

Top
 Profile  
 
 Post subject:
PostPosted: Wed Aug 04, 2004 4:21 am 
Offline
User avatar

Joined: Mon Aug 02, 2004 7:59 am
Posts: 338
Yup.... it sounded a bit wierd to change the oil on every evacuation....


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 22 posts ]  Go to page 1, 2  Next

All times are UTC


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB © 2000, 2002, 2005, 2007 phpBB Group